• Hi all and welcome to TheWoodHaven2 brought into the 21st Century, kicking and screaming! We all have Alasdair to thank for the vast bulk of the heavy lifting to get us here, no more so than me because he's taken away a huge burden of responsibility from my shoulders and brought us to this new shiny home, with all your previous content (hopefully) still intact! Please peruse and feed back. There is still plenty to do, like changing the colour scheme, adding the banner graphic, tweaking the odd setting here and there so I have added a new thread in the 'Technical Issues, Bugs and Feature Requests' forum for you to add any issues you find, any missing settings or just anything you'd like to see added/removed from the feature set that Xenforo offers. We will get to everything over the coming weeks so please be patient, but add anything at all to the thread I mention above and we promise to get to them over the next few days/weeks/months. In the meantime, please enjoy!

Dust Extractor Remote Control

Duncan A

New Shoots
Joined
Nov 9, 2016
Messages
106
Reaction score
41
Location
Northampton
I have an Axminster ADE2200 dust extractor (really a chip extractor) with a 1.5kW motor. It has a starter with NVR so if the power is interrupted and then restored, the motor will not start unexpectedly.

Having moved it some distance from where I normally work, it is less conveniently to hand than it was, so I have looked into fitting a remote control of the sort that can be bought on eBay or Amazon for a few quid.
The R/C socket that I bought claims a max load of 2.9kW so should be OK for the job as long as the startup current doesn't kill it after a few uses.

As a trial, I inserted the R/C socket between the contactor and the motor so that the undervolt/hold-on coil is unaffected, and other protection devices also remain operative. As I switch off all sockets not in actual use, when I start work I first need to switch on the wall socket, then press the Start button on the starter to pull the contactor in. It remains held in by the hold-on coil and the DX starts and stops on command using the R/C.
This all works well, but there is a moderate buzzing from the contactor/coil assembly which is probably present when the DX is running, but can't be heard, so I wasn't aware of it. I know that such a buzz is quite common, but operating in this fashion means that the coil will be energised for much longer periods than previously, when it was only energised while actually running the DX.

Average "On" hours in this mode will probably be a max of 4 hours in any given day, and an average of only about 1 hour/day over the year.
My question is this: Given that the electrics are relatively cheap Chaiwanese components, am I likely to materially reduce the life of the coil or the contacts by doing this?

All comments and advice welcome
Duncan
 
Duncan,

It is not unusual for contactor coils to buzz and as you say the noise is often masked by the motor. Nothing to worry about.

The relay in your RC socket will be going through hell at each start up with inrush currents of around 40 amps each time but could survive quite a while with just hobby use. Otherwise use the RC socket to drive another contactor in between the NVR and the motor for a long lasting design.
There is another way using a small relay for the NVR function and the existing contactor coil and get rid of the buzz annoyance at the same time.

Bob
 
Thanks Bob
Your second suggestion appeals to me and I may give it a try. For now, the R/C has been stolen by SWMBO so not much I can do until I get another one!
Duncan
 