On a recent purchase of a machine imported from the US I had a big motor (3hp) designed for 240v ac and 60Hz (the American mains frequency) In UK we have a 50Hz supply and so the motor needs a reduced voltage in proportion to the frequency change. So I needed 200v. Some motors are designed to be able to cope with a frequency change and no voltage change but cheaper motors don't have that design margin and my motor ran far too hot on 240v.
The tool for the job is a transformer.

One way is to have a transformer designed simply for 240v input and 200 v output. This would be a custom design and be very expensive. Using this method, the transformer needs to handle the full power of the motor, making it big and heavy - approximately the same size again as the motor.
However there is another way to step the voltage down (or up) as needed.
I was talking to a friend about this and whilst he had heard of it - he was unsure how it works so I thought I would write it up here. I hope it is of interest.
Here is our incoming 240v mains supply.

and graphically this is a sine wave voltage like this

Now we add a transformer but one that produces the DIFFERENCE in the voltages that we need ie 40v. It still needs to deliver the current needed by the load but because the voltage is lower, the size, weight and cost is lower and in most cases will be a stock item you can buy.

and graphically

If the two waveforms are added together like this

the result is the Green sine wave which is 280volts
The circuit is below

If we connect the output of the transformer the other way round we get a reduction in the voltage

This is because the 40v is inverted or 180 degrees out of phase. Graphically the peaks of the blue line now line up with the troughs of the mains waveform and so the voltages subtract.

You might see our American cousins refer to this method as "buck" (step down) or boost (step up)
Hope this might be of interest.
Bob
The tool for the job is a transformer.

One way is to have a transformer designed simply for 240v input and 200 v output. This would be a custom design and be very expensive. Using this method, the transformer needs to handle the full power of the motor, making it big and heavy - approximately the same size again as the motor.
However there is another way to step the voltage down (or up) as needed.
I was talking to a friend about this and whilst he had heard of it - he was unsure how it works so I thought I would write it up here. I hope it is of interest.
Here is our incoming 240v mains supply.

and graphically this is a sine wave voltage like this

Now we add a transformer but one that produces the DIFFERENCE in the voltages that we need ie 40v. It still needs to deliver the current needed by the load but because the voltage is lower, the size, weight and cost is lower and in most cases will be a stock item you can buy.

and graphically

If the two waveforms are added together like this

the result is the Green sine wave which is 280volts
The circuit is below

If we connect the output of the transformer the other way round we get a reduction in the voltage

This is because the 40v is inverted or 180 degrees out of phase. Graphically the peaks of the blue line now line up with the troughs of the mains waveform and so the voltages subtract.

You might see our American cousins refer to this method as "buck" (step down) or boost (step up)
Hope this might be of interest.
Bob